Skip to content
Home Inspection Software
home inspection software photo editing view nachi home inspector association Home Inspection Software allowing you to create easy to read, customizable reports that can be uploaded online, emailed, or printed out on the job site. Runs on Windows, Mac & Linux!
ASHI home inspection software screenshot.png Create a professional looking home inspection website for $20-$25 a month. We give you all the tools you need to create a site and get it to the top of the search engines. No previous skills required!
You are here:Home arrow General Discussionarrow Inspection Discussionarrow Water Heater TPR piping
Home Inspector Pro Inspection Software
August 20, 2008, 07:43:42 AM *
Welcome, Guest. Please login or register.

Login with username, password and session length

There are currently 0 users in chat
News: Welcome to the brand new Home Inspector Pro Forum. Please feel free to ask any questions and help get the discussions rolling.
 
   Home   Help Search Chat Login Register  
Pages: [1] 2 3   Go Down
  Print  
Author Topic: Water Heater TPR piping  (Read 1868 times)
David A. Keating
Jr. Member
**

Karma: 4
Online Online

Posts: 97



View Profile WWW
« on: May 14, 2008, 11:37:24 AM »

Other than installing a sump pit with an automatic pump does anyone have any ideas where an older home does not have a floor drain to pipe the TPR to?
Logged

Jay Markanich
Location: Bristow VA
Sr. Member
****

Karma: 7
Offline Offline

Posts: 254



View Profile WWW
« Reply #1 on: May 14, 2008, 07:10:04 PM »

Dave - I see older homes all the time, many very historic, like early 1800's.  Often there is no floor drain.  Since the TPR seldom discharges, or when it does there is such little water, I have seen everything from brownie pans to hoses into buckets.  Neither really bothers me, so long as the buyer understands what is going on.  New codes around here are different - there must be a discharge location - but they don't grandfather.  What is your issue?  Is someone asking a question or trying to fix a problem?
Logged

www.jaymarinspect.com
Northern Virginia Home Inspector
Jay Markanich Real Estate Inspections, LLC
Northern Virginia Home Inspector
Festina Lente - Make Haste Slowly
David A. Keating
Jr. Member
**

Karma: 4
Online Online

Posts: 97



View Profile WWW
« Reply #2 on: May 14, 2008, 08:00:58 PM »

Recently, it came up on a 1800's home. I had to point it out, and when asked why I had to explain the possibility if the TPR valve opened and did not close, of course the basement could flood. A sump would be very expensive, piping up-hill is not a good idea..............was hoping someone had an easy out to calm them down.
Logged

Bob Elliott
Jr. Member
**

Karma: 4
Offline Offline

Posts: 87



View Profile
« Reply #3 on: May 14, 2008, 10:57:53 PM »

so out the wall is not possible , I take it?
Logged
Jay Markanich
Location: Bristow VA
Sr. Member
****

Karma: 7
Offline Offline

Posts: 254



View Profile WWW
« Reply #4 on: May 15, 2008, 04:30:17 AM »

Bob's idea is good, but you'd have to see the house to make suggestions.  I think maybe you put an image into their heads.  Sometimes I see something like that and mention it to the buyers with the caveat something like, "it doesn't look like anything like this has ever happened, and it is very unlikely that it would, but the worst case is..."  You know what I mean.  The image is there, but not prominent.  There are those little pumps put beside some basement AC units to pump out condensate - the ones I see are blue. They are small, connected to a 1/2" plastic tube, and can pump an indefinite distance.  That's probably the best solution, but I haven't seen the house.  I tell people to put a quarter cup of Clorox in them each year because they get goopy.  Now you need an electric source...
Logged

www.jaymarinspect.com
Northern Virginia Home Inspector
Jay Markanich Real Estate Inspections, LLC
Northern Virginia Home Inspector
Festina Lente - Make Haste Slowly
David A. Keating
Jr. Member
**

Karma: 4
Online Online

Posts: 97



View Profile WWW
« Reply #5 on: May 15, 2008, 07:33:28 AM »

Yes, out the wall is possible but obviously would be uphill for the piping, (7'-8' basement wall) but that would still be better than flooded basement. I did not dwell on it, only mentioned why we point it out. While not very often, I have seen TPR valves open partially and not close completely. Yes I'm aware of the small condensate pumps, in fact theres one on the furnace right next to the HWH.     
Logged

Bob Elliott
Jr. Member
**

Karma: 4
Offline Offline

Posts: 87



View Profile
« Reply #6 on: May 15, 2008, 08:05:28 AM »

One would have to see it , with other thoughts being drain pans , and blocks.
Uphill is a no no.
Logged
Dominic Maricic
Administrator
Location: Rancho Cucamonga, CA, USA
Hero Member
*****

Karma: 10
Offline Offline

Posts: 1050



View Profile WWW
« Reply #7 on: May 15, 2008, 02:10:11 PM »

Dave, if you have pics, feel free to attach them to your post so others can check them out Smiley
Logged

Dominic Maricic
Home Inspector Pro Home Inspection Software - Lead Programmer & Owner
David A. Keating
Jr. Member
**

Karma: 4
Online Online

Posts: 97



View Profile WWW
« Reply #8 on: May 15, 2008, 03:05:17 PM »

Will do but but this one was pretty cut & dried........old house no floor drain for TPR piping for HWH. I have to note it on the report, cuz if I dont and in this case it would probably be written up by the next inspector as it was a pre-listing inspection. I dont like raising the flag, but dont feel like I got much choice. The best I can do is say something like, "it almost never sticks open and causes any problems, but you never know and it's my job to point it out to you"

Here's a good one though!!!!!!!
This same house had multiple wires under on lug on two different breakers, (the panel was full) and I noted it on the report. Also there was a 14awg on a 20amp breaker. When I went back this morning to retreive a radon monitor the remodel contractor replaced these two breakers with 50 amp breakers! 
Can you top that! 
Logged

Jay Markanich
Location: Bristow VA
Sr. Member
****

Karma: 7
Offline Offline

Posts: 254



View Profile WWW
« Reply #9 on: May 15, 2008, 03:53:19 PM »

Can't top it unless I had time to think about it - we've all seen some weird stuff.  At least with the 50 amps the wiring is covered.*  The breakers won't get hot...!  I had a new home the other day where the kitchen light switch turned the fridge on and off.  You have to try real hard to do that.  For all I know, the "electrician" was Paco, of "zapped electrician" fame.  I had in my notes that there appeared to be a short in the fridge, odd for a new appliance, but it can happen.  Then, later, I turned on the light switch and heard the fridge turn on.  Serendipity!
* Home inspector joke, which the County guys never seem to appreciate....
Logged

www.jaymarinspect.com
Northern Virginia Home Inspector
Jay Markanich Real Estate Inspections, LLC
Northern Virginia Home Inspector
Festina Lente - Make Haste Slowly
David A. Keating
Jr. Member
**

Karma: 4
Online Online

Posts: 97



View Profile WWW
« Reply #10 on: May 15, 2008, 04:06:24 PM »

I laughed out loud on that one!
Ironically, this guy that did the 50amp trick was named Paco also! This same guy got up on the house and pulled the service wire tighter at the weatherhead to raise the serivce wires that were almost touching the roof of the detached garage he put up. I said, "man, did you go up there and work on that, dont you know you could have fried, you should have called the power company", he said yeh, I was careful.
I'm still one up on you!
   
Logged

Jay Markanich
Location: Bristow VA
Sr. Member
****

Karma: 7
Offline Offline

Posts: 254



View Profile WWW
« Reply #11 on: May 15, 2008, 04:20:13 PM »

Dees ees jhao wee duu een Neecaragwa, ok man dude?  Eet ok now, ok?  ˇAbrazos!

Now, if you could get him to do it in the pouring rain... well, at least he's up on the house, so he isn't grounded...*

*Another home inspector joke, which the County guys never seem to appreciate....
Logged

www.jaymarinspect.com
Northern Virginia Home Inspector
Jay Markanich Real Estate Inspections, LLC
Northern Virginia Home Inspector
Festina Lente - Make Haste Slowly
David A. Keating
Jr. Member
**

Karma: 4
Online Online

Posts: 97



View Profile WWW
« Reply #12 on: May 15, 2008, 04:45:51 PM »

I just added a new narrative in my Electrical Section, warning that any deficiencies need to be evaluated by a qualified, licensed electrician. Hopfully that covers me now.
I had no clue this guy would crawl up on the roof and screw with this. I cant think of how I would have felt if he would have been hurt or worse. Unbelievable!
Logged

Jay Markanich
Location: Bristow VA
Sr. Member
****

Karma: 7
Offline Offline

Posts: 254



View Profile WWW
« Reply #13 on: May 15, 2008, 05:31:19 PM »

Dave - I lived in South America for 2 years.  Some of the things they do there are amazing.  They live with it.  Unfortunately, some of the things they do are really dangerous and not smart, to say the least.  They would heave a copper wire to hook over cables between light poles to steal power.  That bare wire would come into a bedroom window, was hot all the time, and they would rig it into some transformer in the house to use it for appliances or a jury-rigged outlet.  They had these small heaters for the shower, wired into one of those handled u-shaped devices that would lower into a sleeve to close the circuit and heat the water (old school).  It was exposed, right beside the shower and if water splashed on it, well, it splashed.  Children (!) used light-bulb sockets hanging from the ceiling to insert cables, taped in place, which they would connect directly to other things - a radio, fan, even a television.  An oven and a fridge would both be inserted, by the ends of improperly-sized, bare wires, into a 220 outlet on the wall, and used at the same time.  I saw this stuff all the time.  It is a way of life.  Your friend on the roof is just doing what he knows.  It is what it is.  My "zapped electrician" acquaintance was probably doing the same thing the next day, in the rain.  It is what it is.
      When I see odd electrical, it prints out as a very BOLD item on my report (the report on my website is a real inspection, bold items and all).  Bold, my report says, indicates a condition that is dangerous, unprofessional, expensive and/or can affect habitability.  There is a disclaimer which prints that says all BOLD items need to be checked by a qualified technician.
      I just this evening got an email from a client for whom I did an inspection last week.  She was not present, her mother was there.  At the inspection I noticed some weirdly replaced aluminum siding with a 1" hole in it.  There was what appeared to be an outline on the patio from a hot tub, but not recent.  In the panel box there was an unused hole from a previous, removed  breaker, and a large cable was still connected to the lugs.  The cable was cut, rolled up inside the box, and terminated with electrical tape.  This is a house, short sale, quickly put on the market to prevent foreclosure.  The seller spoke Spanish to his agent, not knowing that I was understanding.  He said some things he should not have said, about the hot tub and other things that were behind walls and such, saying that I would never find them.  The agent "translated" what was being said for the buyer's mother, explaining how the seller wanted everything in the house to be perfect for her daughter, and to please let him know what he could do for her.  Yes, he was lying, very smoothly, smile on his face.  I could have puked.  I deserve an Oscar for hot revealing how I wanted to remove his face...  My client was being totally set up.  This agent is worth his weight in navel lint, and I have been in touch with the local board about him.
     There is a much longer story, but this is a nub for your interest.  Bottom line - my client, a veterinarian in Massachusetts, emailed me to thank me profusely for my report.  The County is coming down on this house.  My client and myself are both protected by the BOLD on the report.  Unfortunately, I see houses like this, sold by people like this, three or four times a week.  It is a huge problem.  "Electricians" and "plumbers" and "HVAC specialists" and, and, and are everywhere and you and I have to protect ourselves. 
     It is what it is.
Logged

www.jaymarinspect.com
Northern Virginia Home Inspector
Jay Markanich Real Estate Inspections, LLC
Northern Virginia Home Inspector
Festina Lente - Make Haste Slowly
David A. Keating
Jr. Member
**

Karma: 4
Online Online

Posts: 97



View Profile WWW
« Reply #14 on: May 15, 2008, 06:28:09 PM »

In 1970 I started out in the industry, (after a couple years with a very small volume builder in Iowa) as a framer here in Denver with a good sized family owned builder.
The company sold & closed about 3-5 homes a week. Ranches, tri-levels and two-stories with a max of about 2000 sq. ft.
Of the 5-8 crews consisting of 4-6 men per crew there was one only one guy, (who was on one of my crews), who was not the typical construction guy from the midwest or similar. He spoke English, was polite, considerate and loved America.
Now as you say,
It is was it is. 
Logged

Pages: [1] 2 3   Go Up
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.5 | SMF © 2006-2008, Simple Machines LLC
Joomla Bridge by JoomlaHacks.com
Valid XHTML 1.0! Valid CSS!